Oil furnace testing
Dirk Wright
Member Posts: 142
I have been reading and reading about oil burning equipment, and I was wondering how techs start the oil burner if the furnace or boiler is in the basement and the thermostat is upstairs? Do you run up and down the stairs changing the thermostat setting to get the furnace to turn on? I was considering just jumpering between the "R" and the "W" terminals on the burner controller, is this OK? As I understand it, the thermostat merely sends a 24 vac signal to the "W" terminal when there is a call for heat, but I don't want to destroy my thermostat by jumpering the conections at the furnace instead.
Just
remove the thermostat wire from the "R" terminal so you do not fry anything. If you remove any other, the power is still being fed to the stat.
Remove "R" and jumper R-W
Mitch0 -
Thanks!0 -
make sure you remove the jumpers when ypur done or you'll be back for over heating0 -
and
Make sure to test the t-stat after it's all said and done!!0