Honeywell L8148 Aquastat
Options
Rob_31
Member Posts: 17
Hello. I had a pipe leak water into my Aquastat relay, and it tripped the breaker on the furnace. I took the knobs off the low, and high limit, removed the cover, and then dried and cleaned it out. The boiler works well now, but I didn't mark the knobs when I took them off, thinking that they were somehow keyed to go on only one way. Turns out the shafts were just splined, so the knobs could go on any old way. So I played around, and watched the operation of the boiler, and got the low and high limit knobs sort of close to where I think they belong. Is there an easy way to line them up?
Here is how I think the relay works - please correct me if I'm wrong. I have a tankless water heater.... with no call for heat, it seems to cycle on low limit to turn on, and off by the differential setting. With a call for heat it will turn on at low limit, and off at high limit. That's how it seems to work, but if someone could tell me how it really functions, I'd appreciate it.
Thank you, Rob
Here is how I think the relay works - please correct me if I'm wrong. I have a tankless water heater.... with no call for heat, it seems to cycle on low limit to turn on, and off by the differential setting. With a call for heat it will turn on at low limit, and off at high limit. That's how it seems to work, but if someone could tell me how it really functions, I'd appreciate it.
Thank you, Rob
0
Comments
-
Honeywell L8148 Aquastat
Hello. I had a pipe leak water into my Aquastat relay, and it tripped the breaker on the furnace. I took the knobs off the low, and high limit, removed the cover, and then dried and cleaned it out. The boiler works well now, but I didn't mark the knobs when I took them off, thinking that they were somehow keyed to go on only one way. So I played around, and watched the operation of the boiler, and got the low and high limit knobs sort of close to where I think they belong. Is there an easy way to line them up?
Here is how I think the relay works - please correct me if I'm wrong. I have a tankless water heater.... with no call for heat, it seems to cycle on low limit to turn on, and off by the differential setting. With a call for heat it will turn on at low limit, and off at high limit. That's how it seems to work, but if someone could tell me how it really functions, I'd appreciate it.
Thank you, Rob0 -
Rob, I know this is not going to be the answer you want to hear but for your safety please consider theses words come from the heart of a professional.
If the control has been subject to water damage it should be replaced the safety, accuracy and reliability of the control is no longer guaranteed nor should it be expected.
I understand it may be working now but please for your and your familys safety get the control replaced.
Best of luck to you.
Your friend in the industry,
Alan R. Mercurio
www.oiltechtalk.com
0 -
Ok, thanks. I'll replace it.0 -
Thanks
Thank you for the reply. I will get it replaced.
0 -
You're very welcome and thank you for understanding my concern.
Your friend in the industry,
Alan R. Mercurio
www.oiltechtalk.com
0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 130 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements