how many GPM (from a shower) can go thru a 2\" trap?

Options
Bruce_9
Bruce_9 Member Posts: 6
I am installing a Grohe 3/4" shower valve and five 2.75 Gpm shower heads and body sprays. What about the drain for this hot water guzzler? How many GPM will go down a 2" trap before a lake forms in the shower? All the code books and references I have only talk about fixture units which I don't think applys here. Are there any engineers out there who know or know of real reference books that address this situation? Maybe there is a standard for school gym showers or other high volumn cases? Thanks in advance for your help.

Comments



  • 6-1-05 i have a power vent water heater to instal .with a inspector promblem the inspector says code for flew termanation has to be 10ft away from property line .manafactures say 2ft .today i ascked him to show me the code so we spent 1/2 hr looking in code book with know luck.code book direct vent b vent z vent refer to manufactures recamendatoins please help thank you
  • hr
    hr Member Posts: 6,106
    Options
    The strainer is

    usually the bottle neck in the flow. I know a 2" drain easily handles a garden hose at full flow :) Of course the P trap is properly vented? :)

    Unvented traps can be REAL slow.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • PLUMBERPIERCE
    PLUMBERPIERCE Member Posts: 9
    Options


    Plumber with water heater problem: I'm in Mass, and can only speak for our state code. In terms of gas equipment manufacturer specifications supercede state code. Start by calling them for verification. Then present their recommendation to the inspector
  • Al Letellier
    Al Letellier Member Posts: 781
    Options
    shower drain

    I have a Moen 5 head unit in my personnal shower and even with all five going, a 2"drain handles it with no back up whatsoever. Check your local code. Here in Maine a 2" drain is all that is required, and the fixture units are described as the force exerted on a plumbing system by the flow of water from any fixture as determined on some arbitrary scale....if you know who or what "arbitrary" is, let me know.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • gerry gill
    gerry gill Member Posts: 3,078
    Options
    the ASPE data book

    the data book #2 from american society of plumbing engineers says a drain should flow 1/2 full for best effect..at a 1/4'' pitch, 1/2 full flow on a 2'' drain is limited to 8.4 gpm...can you ''stuff'' more down it? sure..but then you mess with the air that is desired over the flow..the idea is to not have a ''slug'' of water moving down the pipe..i would recommend either two 2'' drains or one 3'' drain...hope this helps..
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Options


    Exact situation. 2" properly vented drain is more than adequate.
  • hr
    hr Member Posts: 6,106
    Options
  • Michal
    Michal Member Posts: 213
    Options
    since when did manufacturers codes superceed

    I am totally un aware that manufacturers specs superceed state codes, I thin you are wrong wirth that. State codes are more stringenrt then any manufacturers code, and yes you should be 10'-0" away, but thats all in your states mechanical code section or might be under nfpa codes as well
  • Jack_21
    Jack_21 Member Posts: 99
    Options
    Yeah, cool info Gerry, Thanks!!

  • PLUMBERPIERCE
    PLUMBERPIERCE Member Posts: 9
    Options


    Where did chimney venting go, who gave us fan assisted venting, sealed combustion. Pex tubing, cssr gas tubing... The manufacturers did. when the product is approved by the code and governing bodies, until its documented in the text we refer to the manufacturers specs. until just this march there was no mention of some of the products listed above in our code we followed the manufacturer's specifications. as long as the venting meets the manufacter's specs on both sides of the property line, [ie] walkways, windows , doors, forced air inlets so forth wheres the problem? The building isn't ten feet from the property line!!! curious
  • dasplumber
    dasplumber Member Posts: 6
    Options
    make sure you use wide mouth strainer on drain!

    2" drain is fine but make sure that you use a 6" wide strainer. We have had drainage problems in the past with the smaller 3"-4" strainers. The 6" strainer is money well spent.
  • Bruce_9
    Bruce_9 Member Posts: 6
    Options


    Who makes these shower pan fittings with 6" strainers I have only ever been able to get 4" from my wholesalers?
  • Michal
    Michal Member Posts: 213
    Options
    I have never seen 6\"

    but look into J.R. Smith, it might be a floor drain and not a shower drain with a brass top, thats all I can think of
  • Scott Denny
    Scott Denny Member Posts: 124
    Options
    Code question

    Bruce
    In UPC territory, the first head is rated at 2 drainage fixture units (DFU)[table 7-3]. The next four heads are rated at 1 fixture unit each. Thus, you have a total of 6 DFU's. Maximum loading for a 2" trap is 4 DFU's and for a 3" trap 6 DFU's (section 702.0). Therefore, I would be required by code to put in a 3" trap and drain. In reality, most inspectors would not go to the trouble of counting DFU's, so a 2" drain would probably fly.