Mixing w/ reset

on a boiler that is using outdoor reset will there be problems w/ overshooting? I have heard that you should not mix the two because the 3 way will not "understand" the reduced water temp therefore give too high a water supply to the panel/slab that you are trying to mix down...kpc

Comments

  • Dan Peel
    Dan Peel Member Posts: 431
    Style

    Your results will depend on the type of 3 way you are using. A three way thermostatic will try to maintain it's preset outlet temperature regardless of input water temperature. A proportional three way valve is flow based and can follow a source reset. Enjoy....Dan

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • hr
    hr Member Posts: 6,106
    Keep in mind

    with a 3 way thermostatic you will nee about 20 degree warmer water in the primary, or boiler loop to make them operate, and mix properly. Still my choice.

    An non motorized manual 3 way ( dumb valve :) will not respond properly to changing loads. It mixes on flow only. So if it is connected to a radiant manifold with numerous telestat operators, for example, as more zones open the mixed temperature changes. A semi proportional reset, so to speak!

    Just depends on your application how tightly you want to keep that temperature, and amount of control you need.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"