Banging/Knocking hot water baseboard heat
Well I have loud pipes. For the last 12 years. My solution has been to cut the heat off at 11 pm and turn it back on at 7 am. Now that we are selling the house we are trying to fix it. Its not a ticking like the fins rubbing. Its a loud knocking that is very quick, one after the other, then slower, then slower, then stops. I've combed the fins, we've bled the system (although I do note that there are no upper level bleeders, must be done from the basement). I've chiseled out around the pipe, I've lifted the pipe, moved the pipe, left, right, up down. Kicked it in frustration several times. Shoved plastic shims in the floor holes. I've changed the temp on the boiler up and down, nothing. Finally we opened up the ceiling underneath where we thought the banging was coming from. Seemed ok, but we installed an accordion joint. Still nothing. I'm going bonkers. I really don't want to tunnel out my entire living room ceiling. Its two zones, this is the second floor. The first floor is wonderful. The second is the issue. It supplies plenty of heat, just loudly. Also I've noticed that when the system is cold, it doesn't really happen. It happens when the system is cycling on and off. So for example in the morning when it has been off all night, I turn it on and its ok, but then when it cycles off and then back on it bangs every time. The two zones each have their own circulator pumps. Is there anything I can do beyond ripping out of my ceiling to expose the pipe? Anything that can be installed to dissipate the noise? Help? Anything?
  • Ironman
    Ironman Member Posts: 7,367
    Are there any zone valves on the system?
    How about posting some pics of the boiler and its near piping from a few feet back?
    Bob Boan
  • bcantrell17
    bcantrell17 Member Posts: 10
    Thanks for your response. I'm not sure. Aren't zone valves for if I don't have individual pumps per zone? I'll take some pics the best I can, not a lot of room in the utility room. Be right back.
  • bcantrell17
    Jamie Hall Member Posts: 23,162
    That is classic expansion noise. Really classic! The solution is to find the pipes which are rubbing on something as they expand, and either shift the hangers slightly so the don't rub or slip a piece of polyethylene -- a plastic milk jug is ideal -- between the pipe and whatever it is rubbing on. Should fix it right up. However, if you can't get at the pipe you may be out of luck.
    bcantrell17
  • bcantrell17
    That's what I was afraid of. Thanks for confirming. Unfortunately it will require ripping out the entire living room filing to find it! Thanks again.
  • Ironman
    Can you get the full model number off of the circulator's data tag? It's on the electrical cover of the pump.
    Bob Boan
    HVACNUT Member Posts: 5,804
    edited February 2017
    Like Jamie said, definitely sounds like expansion noise. You don't hear it on the first cycle in the a.m. because it's a cold start aquastat and the circ runs pushing cold water through the loop, then slowly heats, avoiding that rapid cold to hot expansion that you get on later cycles. The easy fix is... play some Metallica, loud.
    bcantrell17
  • MikeL_2
    MikeL_2 Member Posts: 486
    You could try constant circulation with outdoor reset including a low loss header or another type of primary/ secondary near boiler piping. Outdoor reset would reduce the rapid expansion that occurs when ambient temperature water is replaced by high temp boiler water........
    bcantrell17
  • bcantrell17
    Iron Man, the # is Taco 007-F5
  • bcantrell17
    HVACNUT, that has been the other half of my band-aid solution!
  • HEATON
    HEATON Member Posts: 117
    have you checked the temp leaving the boiler? I had one that was making steam cause the controls failed and gauge was unreliable? Definate agree w/constant circ with or without O>D> reset. Things that go bump in the day, " Scarey" john
    bcantrell17
    EBEBRATT-Ed Member Posts: 15,453
    Shut the boiler off and just run the circulators if you can. Is it quiet?? This will tell you if the noise is related to changes in water temperature or not.
    bcantrell17
  • Mike
    Mike Member Posts: 94
    Have you checked the air charge, in the expansion tank? Had a system doing the same as yours, the tank had lost it's charge. Pumped it back to the proper pressure, and all was quite.
    bcantrell17
  • bcantrell17
    Yeah, I've ran it at the lowest temp on the boiler and it still banged. Thanks.
  • bcantrell17
    I'm not sure if I can do that... I'll give it a shot. Thanks
  • bcantrell17
    I thought the pressure was fine, but I will check the expansion tank. Thanks.
  • bcantrell17
    This is a very technical response! I will have to forward it to someone that understand this better than I. Thanks for your response!!