Trying to plan vent run for 76k btu power vented HWH, and hearing different opinions on venting.
Some say I can run the 3" pvc vent the 27ft up above roofline strapped to exterior of house.
Some say the blower will not be able to push out the cold dense air in colder months and will have massive condensation to manage.
Any ideas on this? Can it be done? Insulate the vent pipe?
Thanks

Comments

  • John Mills_5
    John Mills_5 Member Posts: 951
    Options
    Find the I/O manual for the brand you are thinking of and see what they say. It will vary.
  • 4Johnpipe
    4Johnpipe Member Posts: 480
    Options
    Relatively certain most if not all manufacturers would recommend to limit the amount of piping exposed to the elements...Flue gas condensation is not your friend in winter...