boiler burners, flame and pressure
aircooled81
Member Posts: 205
When the manufacture calls for 3.5" manifold pressure, what is the lowest pressure to allow at the manifold?
I have a boiler that has the yellow tips of the flames touching the cast iron sections of the boiler, and I am thinking of adjusting the burner pressure lower, to lower the flame height with-out losing blue flame.
Any suggestions?
Any suggestions?
Usually 3.5" is the maximum. Check the burner tubes, make sure they're clean inside and out. Do this before making any adjustments.0
Without the proper equipment to monitor pressure (which should be what the manufacturer calls for, within a very small margin) and the combustion -- CO, CO2, excess O2, temp, all that good stuff -- playing with burner settings is chancy at best. IMHO.Br. Jamie, osb
cleaned the burners, checked gas pressure with manometer.
no combustion gas analyzer, so the consenses is leave it at the manufactures spec - or the posted spec on the nameplate is the max.
any opinions on flame height and impingement on the cast iron sections?0 -
If you don't have a combustion analyzer you're wasting your time.To learn more about this professional, click here to visit their ad in Find A Contractor.0
Agreed. Sure, analyzers aren't cheap, but they're much cheaper than lawyers.Robert O'Brien said:If you don't have a combustion analyzer you're wasting your time.
Consulting0 -
Can you recommend a good model analyzer?
I looked at and have used the filedpiece sox3, but it doesnt do co.
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
