Placement of Water to air heat exchanger

Options
rico7467
rico7467 Member Posts: 40
Is it more efficient to place my heat exchanger before the a-coil and blower oron the intake side of my horizontal airhandler or on the outtake side of the air handler after the blower

Comments

  • Ironman
    Ironman Member Posts: 7,376
    Options
    It should be placed on the supply side. Most blower motors cannot take the heat produced from the hot water coil. They are designed to have 70* return air to cool the motor, not 140*+ air that will come off of the hot water coil.