Copper sizing for propane install
3/4"0
@hatchet: how can you give a line size when the OP didn't state whether it was the high pressure, medium pressure or low pressure line? He also did not state what the future load for the outdoor bldg. would be. All these unknowns would be necessary to make a correct determination.hatchet said:3/4"
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Oops, I accidentally hit post before I was done. Add, it's depending on the total BTU requirements for the stove, water heater, BBQ & dryer. Knowing outgoing pressure is also important. Undiluted Propane with inlet pressure of 11" in w.c., pressure drop of 0.5 and specific gravity of 1.50 at 80ft. 3/4" steel pipe will give you 212,000 btu per hour.
If your btu demand is higher than 212, and, there is an excessive amount of bends in system, you might have to be at 1" .0 -
Thank you, I do not have the tot of all btu of all appliances,running the gas line as a favor to a friend. I will keep the bends to a minimum. I am thinking of running a direct line in 3/4 csst to HWH tee-ing off the main line to stove , dryer and bbq.there is no tank there yet, is a small house being remodeled.
You MUST find out the load, pressure drop AND the pressure at the outlet of the regulator. Also, using CSST would negate using 3/4 inch. There is a lot of restriction through CSST than in black steel pipe.
Not having the Propane chart in front of me, I can tell you it's (I'm estimating) almost half of what steel is.
Be careful what your fooling with there fella....0 -
Do you have a CSST certification? You should have gotten a book with the class. The three ways to do it are in the manual and how to size it.
There's a lot more to it than you have outlined.0 -
I Recently added propane to our lake house. We have a 500gal above ground tank. After the 1st regulator, They ran a 3/4" yellow jacketed copper through a 1-1/4" conduit that i had buried underground to house. At the house, it transitions to 3/4 Black Iron - 25' & (4) 90* els - to 2nd regulator. After regulator, they used a bell transition to go to 1" Black Iron. 2 x 1/2 tees outside for grill & any additional needs, 1 more 90* then inside for about a 6' Branch to feed all inside needs including A 3/4" line to our 199,000 btu tankless, 1/2" to future Dryer, 1/2" to future stove, 1/2" to Garage & 3/4" to future gas furnace Hookup for when the HeatPump goes.Winter Park, CO & Arvada, CO0
While not rocket science gas line distribution is something determined by formulas. what you are asking is can something designed for one thing be modified arbitrarily. short answer NO . do not even Think about that. You need someone with the advantage of a book. unless you carry the formulas around in your head for pipe sizes and lengths over 200 feet long then i will concede that by also knowing a variety of other information you could get it right.
the very few walking who have these stored in their brain through photo graphic memory would still likely resort to a book when designing the new modifications.
Thats my 2 cents.
hope you clearly understand . hire someone who has some gas fitting experience with a licence to back that up. you might not have to die from your efforts that way.1 -
Hi everyone there, Thanks for all the replies. Sorry I've been busy there for a while and I haven't logged in for while.
Icesailor you know what, they did not give me a book with the csst certification!!!
As far of this gas line job, one of our propane gas man told me to run everything in 3/4 black pipe starting off from a manifold, and so I did 2 years later and 2 winters later everything is working fine and they are happy ,the technician from the propane company who came and test the lines and hook up the tank and regulator was impressed , and said not bad for an oil burner technician. They only call me to tune up the oil burner unit, and yesterday their Fathers day BBQ was good.( I happen to be there!)
Thank you all for your Help and concern.1
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
