Viessmann Temp Sensor w/ Caleffi SEP4 Hydraulic Separator??
HydronicRookie
Member Posts: 54
Can the Viessmann LLH sensor easily fit inside the Caleffi SEP4 hydraulic separator sensor well?
Has anyone had any problems with them working in tandem?
Has anyone had any problems with them working in tandem?
0
Comments
-
looks like
a 6mm diameter sensor? about 1/4" bolt size? There are a few different well sizes out there, most US size thermistors are larger 1/2" diameter. The Euro stuff and solar sensors tend to be 6mm.
How close does the sensor match that well?
For sure, use some heat transfer paste, or silicone acoustic grease in the well.
It's easier to find small tubes or bottles of the acoustic paste sometimes.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Sensor.
Install sensor on the outlet of separator to the heating system. Strap on. Even with viessmann LLH it is recommended. All you need is to control temperature of the water to the system.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
sensor location
we show both locations with the separator, in the latest Idronics 15. If you install it on the pipe, be sure to insulate it. I would still use some heat transfer paste.
With both the boiler and system circs running, depending on flow rates, you will get some temperature blending in the separator. I prefer sensors in a well, but the sensor on the pipe downstream would read the "blended" temperature.
Another tip if you ever need to install a sensor on a bolt or pipe is to get a screw lug from an automotive or electrical supply. The early solar tanks had a stud welded onto them for sensor mounting.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Easy enough
Thanks for this. It definitely alleviates concern about a peg and hole mismatch.0 -
Thermal Grease
Great pro tip regarding the thermal grease, will definitely get some and use it in either scenario but also insulate the strapped sensor if I don't end up using the well. Thanks!0 -
blended temperature
Isn't it what we want? Outdoor reset sets system inlet temperature, and this is system outlet pipe on separator. Even on Viessmann's LLH we install strap on sensor , not in the well.Gennady Tsakh
Absolute Mechanical Co. Inc.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements