Honeywell mercury steam valves
Brutus
Brutus Member Posts: 2
I am looking for help troubleshooting valves that are staying open
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Staying open
    Is your system 2-pipe, or 1-pipe?
    I suspect a 2-pipe system, with some Honeywell traps which will not close when the steam arrives.
    Any trap from that period has been designed for low pressure, such as below 1 psi, so is your system operating in that range?
    Check the pressure, and make sure it is below 16 ounces. A good gauge will be needed , from gaugestore.com.
    Replacement capsules are available for traps from tunstall inc.--NBC
    Steamhead Member Posts: 16,843
    Take some pictures
    of these units and post them here. Let's have a look at them.
    Consulting
  • Brutus
    Pics of traps
    That's a Zone Valve
    the mercury switch probably functions as an "end switch" which can do things like start the burner when the valve opens.
    You may be able to get a new head unit for this thing. If not, you'll have to replace the entire unit. We've had good luck with Belimo zone valves on steam- these are ball valves rather than globe valves and don't restrict the steam flow as much.
    Consulting