7284 primary control with power vent
RayH
Member Posts: 98
How is the new 7284 primary control connected with a power vent?
i like to wire the powervent
To break power to the oil valve if the burner in question is equipped. You can wire to break the power to the motor, although a relay may be required to isolate the circuit and prevent short cycling.There was an error rendering this rich post.
Are you connecting L1 to the Limit?0 -
L1 to burner goes to L1 on control
Limit to the burner is from your limit, allows for a post purge on reaching limit or at the end of cycle. What power Venter is it?There was an error rendering this rich post.
I have 4 wires coming into the primary from the power vent. I believe the wires are to be junctioned together some how. In coming power is connected to L1. Should I also connect the limit from the primary to the L1 ?0 -
in general
There is an L1 to the primary, L2 to the primary, power up to powervent control(usually from motor lead on primary) and power back from powervent control to the motor. If this is unfamiliar, a visit from a professional may be in order. There are different variables to each system, it is hard to cover them all over the net.There was an error rendering this rich post.
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 39 Industry Classes
- 15 Recall Announcements
