Does this boiler seem piped right?

Ed59Ed59 Posts: 12Member
I've been reading on this site and Dan's books how important boiler piping is and I'm wondering if this looks right? Or am I confused?
p1.jpg 0B
p2.jpg 0B


  • nicholas bonham-carternicholas bonham-carter Posts: 5,719Member ✭✭✭
    piping problem

    I would say not even close to the instructions. probably should use both headers, and put in a horizontal header with one feed from it to any main above.

    Is the system noisy?
  • FredFred Posts: 2,513Member ✭✭✭✭
    edited March 2014
    Doesn't look very good

    There is no header there. The header should run horizontally 24" to 28" above the boiler water line with a swing joint to relieve stress on the boiler from expansion/contraction. The two mains should each be tied, independently into the header. The equalizer should come off of the end of the header, after the mains, and the piping for the Hartford loop should run along the floor like the wet return and then come up so that there is a close nipple that ties it into the equalizer  
  • SteamheadSteamhead Posts: 9,556Member ✭✭✭✭
    Only thing they did right

    was to use black steel rather than copper. Hopefully you can re-use some of those pieces when you repipe. 
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
  • bustoff315bustoff315 Posts: 26Member
    Auto Feeder

    I find it interesting that the automatic water feeder is shut off as well. I bet there is/was a lot of water leaving that system.
  • Ed59Ed59 Posts: 12Member
    edited March 2014
    Does this boiler seem piped right?

    Like I said, I'm no professional, but this is what struck me:

    - No horizontal header

    - Hartford loop / equalizer boiler side doesn't go down to the level of the return

    - Return not connected to the Hartford loop with a close nipple, looks like 8 - 10"
  • Ed59Ed59 Posts: 12Member
    auto feeder

    Very observant. Wouldn't some it make sense to leave the auto-feeder off most times to make sure you noticed any leakage? Only turn it on if you're going to be away for a while as a safety?
  • Ed59Ed59 Posts: 12Member
    Looking for steam contractor in Boston area

    So this isn't my system. Sigh. I'm looking for a good steam contractor in the Boston area.

    These pictures are right off the Facebook page of one highly rated contractor. They posted them themselves as an example of a job they did.

    But he did measure the radiators. The first contractor I had in (highly recommended by friends) didn't do that. When I questioned the boiler sizing, I was told he had 40 years experience sizing boilers. But the boiler supplier could do a full heat-loss calculation if I wanted...

    Any recommendations?
  • Charlie from wmassCharlie from wmass Posts: 3,331Member ✭✭✭
    I service there

    If it is in CT or MA I service there. You can look at my ad from the link below.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
  • RDSTEAMRDSTEAM Posts: 134Member

    That thing isn't even close to correct. Insulation looks really nice though.
  • Ed59Ed59 Posts: 12Member
    thanks charlie

    I've seen a lot of good advice from you here, but you're a loooong way from Boston. I'd really like to have somebody nearby in case of emergency, and for annual maintenance
  • BobCBobC Posts: 3,026Member ✭✭✭
    This might work

    If you really want someone local you might try

    He is in Milton and he knows whereof he speaks.

    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • gerry gillgerry gill Posts: 2,421Member ✭✭✭
    not even close to right

    Give Charlie a call. He will fix you right up, and properly.