DHW Indirect Air Elimination
ced48
Member Posts: 469
All of the piping diagrams I have seen provide no air elimination provisions in their setups. Is this standard? I am having trouble with air in my DHW loop, should I install something, if so, where, and what?
SMART indirects
come with an air vent. Both diagrams and instructions cover installation.0 -
does the boiler have an air vent?
most mod cons have a vent on the HX. As long as you get the "big air" at the fill and purge, the vent should find the rest and eliminate it.
Got the expansion tank connection correct?Bob "hot rod" Rohr
Living the hydronic dream0 -
HTP Superstor-
maybe not so smart?0 -
Lochinvar Boiler
I added a vent in a cross at the top for pressure release and LWCO-0 -
Air Elimination in Indirect:
Do you have enough pressure in your system? Do you have an accurate 12 to 16# pressure?
I've never seen so much fuss over air elimination as I see here. Any system I ever worked on, once air was purged initially, that was the end of it. Proper pressure will compress air into the water. Don't go by the pressure on the front of the boiler until you prove that it is accurate.
I always put can vents on to shut people up but tightened down the caps tight so they couldn't suck air into the system.
What are some of you doing wrong?0 -
So, Air in the DHW
loop doesn't seem to be an issue very often, so no one adds any air elimination devices?
My system seems to get air into the DHW loop when the heating loop works hard at higher temps, like last night's 5 degrees. The air seems get into the DHW loop and than takes days to work it's way out. I think maybe I need to add a scoop to the loop to take care of the air more efficiently. Any reason not to do this, or am I treating the symptoms, not the real problem?0 -
What size is your expansion device (pressure tank, is it big enough, and is the system pressure high enough?
Like just because you fast fill it to 16#, and don't adjust the pressure adjustment on the fill valve, doesn't mean that the system is running at 16#. And you have to adjust the tank pre-charge pressure to.
I don't mean to sound like a broken record, but I used to turn on and off a ton of houses with all types of systems. In all my years of doing it, installs and services, I never EVER saw all these issues with air that I see here. Its like an epidemic. Do we need to call the CDC about it? It must be contagious0 -
I Did Notice
the system pressure was on the low side this morning, 12 pounds or so- I'll boost it up to 16, and check the tanks pressure-Thank you for your help0 -
Air seperator
If I might suggest - since you mentioned adding an air scoop. I would re pipe it with a microbubble air separator instead of a scoop. There are several on the market. They create a low pressure zone and along with high temperature will allow entrained air to come out of suspension and be removed from the system, a can vent cannot remove air in suspension.
It's been my experience that once you initially purge the system and start circulation the separator will take care of the rest. Within one day in normal circumstances the system will be air free.
Ice is right - if you know what you're doing - pipe um right, start um right and air becomes a no issue.
John Pughe0 -
what type of air eliminator
do you have on the system. the fluid in the DHW indirect loop will at some point circulate through the boiler and heating loop. A few different causes of air problems.
Air elimination device faulty or plugged, not installed properly, PONPC
waterlogged expansion tank
low static fill pressure
entrained air not being removed
restrictive valve or device in piping causing cavitation
There is a lot of value in the modern type micro bubble type of air separators, they trap air and micro bubbles that just pass through scoop type vents. Money well spent.
If the indirect creates a high spot in that piping, not a bad idea to add a float type air vent at the high point.Bob "hot rod" Rohr
Watts AS-MB
on the sytsem-heating loop has no problems with air, quiet. I have had a rattle in the DHW circulator. I was able to get rid of it this morning by closing the isolation valve down enough to cause some disturbance, which shook whatever loose, I assume from the internal check valve. Rattle is gone, maybe it was causing some cavitation,we will see-0 -
maybe pull the circ
if you have good isolation, and check the check! I have see a few of them dislodge from their appropriate resting place and cause flow issues (noise)Bob "hot rod" Rohr
Stupid Me-
After reading icesailor's and hot rod's suggestions, it became obvious that I had screwed something up. Thinking about the fact that the condition got worse after higher operating temperatures, I keyed in on the expansion tank. It was brand new, and large enough, but what about it' s charge, had I checked it? NOT-Added about 12 pounds of air, and presto, all air noise was gone-I guess I assumed it had 12 pounds of air, it only had a couple of pounds, dumb, amateur, mistake. System pressure is now at around 16 pounds, tank has about the same charge, and all is quiet as a mouse. Again, thanks to icesaiior and hot rod for all your help.0