LP gas in cold.....

kcoppkcopp Posts: 1,739Member ✭✭✭
weather. Is there an additive that LP suppliers add to the supply to get it to vaporize better during cold weather? Someone ran this one by me yesterday and is the first time I had ever heard of that....kcopp
·

Comments

  • icesailoricesailor Posts: 7,265Member ✭✭✭✭
    edited January 2014
    Additive:

    Heat?

    Phase Reverser from Star Trek to reverse the laws of Physics?
    ·
  • ZmanZman Posts: 2,333Member ✭✭✭
    Vaporizer

    We used one of these a while back. http://www.algas-sdi.com/vaporizers.html



    There was a persistent low pressure shutdown during high loads. The supply to the building would literally go from 20# to 0# instantaneously.  As soon as the boiler shut down due to low pressure, the supply would go back to 20# just as fast.



    The propane company installed a vaporizer and the problem never reoccurred.

    It never occurred to me before this post, I wonder how much energy the vaporizer uses?



    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    ·
  • Jamie HallJamie Hall Posts: 4,037Member ✭✭✭
    In really cold climates

    the mix which makes up "LPG" can be changed -- more propane, less butane -- to have a higher vapour pressure at any given temperature.  Perhaps this is what was being referred to?



    The vapour pressure of butane drops to 1 atmosphere (0 psig) at -1 Celsius, but propane doesn't drop to 1 atmosphere until about -40 C.  The suppliers change the mix to get a reasonable balance between vapourizing and pressure.
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
    ·
  • Tim McElwainTim McElwain Posts: 3,260Member ✭✭✭
    They will add

    methanol to get rid of possible moisture inside the tanks but it does not change the vaporization. Vaporization will always be less and less as the boiling point of propane is approached -40° F. The lower the volume of fuel and the amount of wet area also affects vaporization. With these extreme temperatures it can really be a tough time with LP.

    As someone mentioned high demand can also be a problem so vaporizers are added to the system, they use the liquid as fuel to vaporize the liquid into a gas. The consumer pays for that, it is really just like a boiler.
    ·