Taco Bumblebee Circulator

I added this circulator on a boiler I installed on my cousins boiler after hurricane sandy. My question is does anyone know how I can pique performance out of it. The boiler is a 3 section slantfin w 1 baseboard zone and 1 indirect hwh as well as a Honeywell outdoor reset. My cousin lost the literature and to be honest didn't fully understand it anyway.



Any ideas or should of I just bought a 007?
·

Comments

  • ZmanZman Posts: 2,339Member ✭✭✭
    Manual

    Here is the manual.

    http://www.taco-hvac.com/uploads/FileLibrary/100-101.pdf

    How are you using it. What mode is it in? Sensor?

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    ·
  • bhop2920bhop2920 Posts: 8Member
    Delta t

    I believe I have it in delta t and its 20 degrees but it comes back I think half maybe less than half even w both zones running
    ·
  • ZmanZman Posts: 2,339Member ✭✭✭
    Sensor

    Is the sensor in the proper location? Is it secured and insulated?

    A 10 degree delta T is not a bad thing. The circ may be running at it's lowest setting.

    Are there performance issues?

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    ·
  • Joe MattielloJoe Mattiello Posts: 512Member ✭✭
    delta T mode

    You might be in the constant speed mode, have you verified your in Delta T?

    for your reference I attached the latest instruction sheet.  Page 3 gives specific instructions on verifying delta T mode. 

    If you have additional questions or concerns, contact Taco tech support at 401-942-8000.  happy to help
    pdf
    pdf
    Bumble bee instruction sheet 102-435.pdf
    0B
    Joe Mattiello
    Application Field Service Engineer
    Taco, Inc.
    ·
  • Joe MattielloJoe Mattiello Posts: 512Member ✭✭
    delta T mode

    You might be in the constant speed mode, have you verified your in Delta T?

    for your reference I attached the latest instruction sheet.  Page 3 gives specific instructions on verifying delta T mode. 

    If you have additional questions or concerns, contact Taco tech support at 401-942-8000.  happy to help
    pdf
    pdf
    Bumble bee instruction sheet 102-435.pdf
    0B
    Joe Mattiello
    Application Field Service Engineer
    Taco, Inc.
    ·
  • Paul48Paul48 Posts: 2,499Member ✭✭✭
    Performance

    As Carl said, is there an underlying issue, that is making you look to the circ.? Uneven heating? A 20 degree DT in a baseboard series loop can give you that. The circ may be running at its minimum, and most of the heat given off at the start of the loop.
    ·
  • Dave HDave H Posts: 166Member ✭✭
    Heat Loss

    Well it sounds like you are here on Long Island or in New Jersey. The heat loss of the house has dropped dramatically. How big is each zone?



    That makes sense since it got a little warmer here the last few days. The BBee is probably running on the lowest speed.

    If the house is warm and comfortable, then you are doing great!



    Dave H.
    ·
  • hot rodhot rod Posts: 4,087Member ✭✭✭✭
    hey Joe

    thanks for the updated manual.



    I've not seen that elevation caution before?



    In addition to pre-charge adjustment the exp. tank may need to be upsized?



    On a 30 gallon capacity system from 12- 20 psi increase takes the tank from 2.8 up to 7.5 gallon expansion capacity, running 60- 180F water temperatures.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    The magic is in hydronics, and hydronics is in me
    ·
  • bhop2920bhop2920 Posts: 8Member
    Thanks

    Yea I have it set for delta-t at 20 degrees but comes back w 10 degree difference. I know I can set to more or less "concentrate" on kilowatt used.



    Secondly I was wondering if the bumblebee circ was overkill



    And thirdly long islands lowest temp would be 10 degrees when I set the osr for that its freezing so I set it for 20 but that doesnt defeat the purpose?
    ·
  • gennadygennady Posts: 529Member ✭✭
    Delta t

    You can try to slow down water flow by playing with ball valve on pump discharge. It might bring pump to the controllable range.
    Gennady Tsakh



    Absolute Mechanical Co. Inc.

    www.AbsoluteMechanicalCoInc.com
    ·
This discussion has been closed.