Trial for ignition

I have a new gas steam boiler Peerless 63-03-SPRK-SP with spark ignition. The burner seems to have a continuous trial for ignition and keeps firing very frequently. Can this be stopped unless there is a call for heat? It is SO ANNOYING, this old house has uninsulated wood floors and I hear every click on and click off.



The burner fires for 2 minutes about every 8 minutes. During the day there is no call for heat, the sun in windows raises the temperature.
· ·

Comments

  • MDNLansingMDNLansing Posts: 297Member
    Hrmm

    Are you saying that the boiler fires up every 8 mins all day long even though the thermostat is not calling for heat? Or, did you mean the boiler TRYS to fire every 8 mins but never lights even though the thermostat is not calling for heat?
    · ·
  • MyName3MyName3 Posts: 4Member
    it is the ignition cycle

    MDN, The spark ignition burner fires up every 8 minutes and runs for 2 minutes. Like clockwork. This is the ignition cycle I am reading about, except it is continuous, not just when there is a call for heat. My house warms up during the day from the sun coming in the window. If I turn up the heat, the burner keeps running longer to reach the thermostat setting.
    · ·
  • MDNLansingMDNLansing Posts: 297Member
    Normal?

    Have you read the manual to see if this is normal? I know on some older electronic ignitions they would do this by design. The pilot thermocouple had to be warm and satisfied twice an hour. It was a diagnostic test. I don't recall seeing any that ran for 2 mins though, it was more like 20 seconds. How new is this install? Have you called the installer and asked them if this is normal?
    · ·
  • MyName3MyName3 Posts: 4Member
    manual

    The manual has the below and there are a number of such articles if you do a Google search. Some posts elsewhere say there are "continuous" such tests that I think means the manufacturer has it set up to keep repeating, rather than just when there is a call for heat. This is the NEW spark ignition gas burners. I'm hoping someone who knows what this technology is about can respond to my post.



    Trial for Ignition – 90 seconds, 5 minute wait between trials for ignition. There is a chart.
    · ·
  • MDNLansingMDNLansing Posts: 297Member
    Make and Model

    What make and model is it?
    · ·
  • Jamie HallJamie Hall Posts: 4,014Member ✭✭✭
    in first post...

    Peerless 63-03-SPRK-SP
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
    · ·
  • JStarJStar Posts: 2,495Member ✭✭✭
    Ignition

    There has to be a shorted control wire somewhere. That should not happen.



    Take the t-stat off the wall. See if it stops.
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac.com
    http://facebook.com/thatcherhvac

    Guaranteed performance. Guaranteed energy savings.
    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    · ·
  • MDNLansingMDNLansing Posts: 297Member
    Agree

    You ave a short, or a faulty module. The ignition should only fire when the boiler calls for heat. What you are describing sounds like the ignition is shorted out and always trying to fire, but the gas valve is shut and not supplying fuel. When no fuel is present to ignite, it will attempt to light for 90 secs and then wait for 5 -6 mins and try again. Sounds like the gas valve is wired properly and the ignition is shorted out.
    · ·
  • MyName3MyName3 Posts: 4Member
    No

    No, MDN, per the first post it is firing for 2 minutes. There is fuel, it turns on for 2 minutes, then turns off.
    · ·
  • MDNLansingMDNLansing Posts: 297Member
    JStar

    Then I point to JStars post. Your reply "The spark ignition burner fires up every 8 minutes and runs for 2 minutes" made me think you were saying the pilot light was igniting but not the full burner.



    Did the thermostat get replaced with the boiler? Has this problem been going on since the boiler was installed or is it something that developed over time? You certainly have a short circuit. Try disconnecting the thermostat and see if it stops.
    · ·
  • nicholas bonham-carternicholas bonham-carter Posts: 5,576Member ✭✭✭
    WWYID-what would your installer do

    Has he any idea about the repetitious short firing?--NBC
    · ·