To get email notification when someone adds to a thread you're following, click on the star in the thread's header and it will turn yellow; click again to turn it off. To edit your profile, click on the gear.
The Wall has a powerful search engine that will go all the way back to 2002. Use "quotation marks" around multiple-word searches. RIGHT-CLICK on the results and choose Open Link In New Window so you'll be able to get back to your results. Happy searching!
In fairness to all, we don't discuss pricing on the Wall. Thanks for your cooperation.
Viessmann & Siggy differ on efficiency at high return temp?
RetroRetro Member Posts: 13
It's very unlikely I can use in-floor radiant in my home bec. crawl is too low clearance to work safely and ceiling is near code min. So I'm sizing alternative emitters, and that depends on return temp. Can live with ~87% but if I'm paying for a mod con why not see if we can still con with radiators or what have you.
Conventional wisdom seems to keep return temps as low as poss for efficiency (and other reasons). For example, Siegenthaler 3rd ed p78 showing curves for a "representative" mod con indicates barely condensing at 125F, even at low fire. And at high fire, maxing out at hardly better than 90% in any case.
But Viessmann eg 222-F manual p3 indicates 95%+ with return temp of 158F at a 30% load. (222-F modulates down to under 20% where I imagine it's even more eficient.) Even at 50% load it seems to be doing some condensing.
Viessmann stipulates 20F drop in emitters - is that a gotcha?
I don't see similar info for Loch or TT, wonder about that.
Viessmann installers in SF Bay area, feel free to contact me via my profile page re whole house remodel
  • SWEISWEI Member Posts: 7,356
    Drop on emitters
    depends on the emitters in question.  10-15ºF is typical on in-floor, modern panel rads can be sized at 25ºF or 30ºF
    Remember, the sizing is done using the average of supply and return temps, so a supply of 145ºF and a return of 115ºF would be sized as 130ºF.  If you size panel rads this way, you will be condensing all season.
  • ZmanZman Member Posts: 3,168
    Chart
    That is one confusing chart! It is not showing efficiency at a particular fixed temp. It is estimating the overall efficiency of a system with a particular design temp,outdoor reset curve and efficiency. The 1.8 or .5 defines the shape of the curve. It is not contradicting siggy's chart. It is a different chart altogether.
    Carl
    Albert Einstein
  • ChrisChris Member Posts: 3,040
    Lamda Pro Combustion
    I'll answer your question with a question? What controls the dew point? If I can control the dew point I can condense pretty much at all times, even above that magical 127-130 degree water temp line.
    Maybe this will help you understand. Its a pretty good little article.
    http://www.thermalsolutions.com/news/wp-content/uploads/2013/04/High-Turndown-Condensing-Boilers.pdf
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."
    edited October 2013
    Deleted
    Good article
    Chris that is a good article.
    I think the original poster was confused about the Viessmann efficiency as it pertains to the heating curves.
    I am saving the article for folks considering Navien.
    Carl
    Albert Einstein
    edited October 2013
    Navien
    Navien does not capture flue gas condensation to reclaim the loss latent heat. While it may condense it still doesn't reclaim lost btu/hr through the venting system. It also does not come ODR unless the installer purchases it separately. Navien, because it has a CAFUE vs an AFUE rating isn't held to the new Sept 2012 standard. That's the story to be told when competing against it. Your correct because he only posted one part of the Viessmann chart h left out the heating curve chart which is attached.
    All boilers have a set of curves like that
    Viessmann is the only one I know of who publishes them widely.
  • RetroRetro Member Posts: 13
    trying to follow your reasoning here...
    Chris and Zman I think I get what you're saying - Siggy's chart is steady state efficiency - do you think the Viessmann chart must be an estimate of seasonal efficiency? I figure, probably heat+hot water for some representative household size in a climate where design temp is -4F.
    Which means, everybody, yes I definitely ought to have posted Viessmann's ODR curves. What is that diagonal scale at the lower left of those curves?
    Room Setpoint
    That's the setpoint the boiler is using to calculate the curve. You could graph the months of the heating season with daily daytime and nightime temps and come up with your operating percentages. Might not be 100% accurate but will give you a idea of where you'd be running most of the heating season.
    Dunkirk has something to say about this...
    Dunkirk's Quantum Leap (discontinued I assume) advertised as follows:
    "Heated condensate (from the Recovery Unit)
    is sprayed down inside the Quantum Leap’s
    Evaporative Re-Cooling Tower where it saturates
    and heats combustion air. This raises the boiler's
    dew point so that 90-plus percent efficiency can
    be obtained at return water temperatures up to
    160° F. The QL is the only residential boiler in
    the world capable of this feat."
    http://dunkirk.dev.salientlink.net/uploads/product/literature/253529d8bd958dd516417653c714da1f.pdf
    While I was looking for availability (doesn't seem to be any) I also found maybe Dunkirk's name should be added to the list of makers with the smallest available mod-con boilers
    http://www.dunkirk.com/product-details.asp?id=247#9
    They come in 50 and 75 kBTU models and have 5:1 turndown
  • StekayStekay Member Posts: 36
    Yeah well, I had this boiler. Maybe that's what ate it alive from the inside out. Actually a great idea with poor execution in my humble opinion. We've learned a lot in 10 years.
Welcome
It looks like you're new here. If you want to get involved, click one of these buttons!