Boiler sizing question

dpeartdpeart Posts: 31Member
So I'm reading and trying to learn this stuff enough to pick someone to replace my boiler.  I ran a couple heat loss calculations on the house.  It has zero attic insulation, zero floor insulation in the crawl space, does have storm windows and 8-10 inch brick walls.  I'm assuming it leaks like a sieve.



I also added up the total EDR for the house (as best as I can) and got 547 x 1.33 = 728MBH which matches the BB14-*-5 boiler in the basement.  It is rated at 705-770MBH.



I then did a heat loss calculation and came up with 240MBH @ 15F, or 303MBH @ 0F.  15F being what VA is rated at.



If I go in and insulate the attic and crawl space, and reduce air infiltration by 50% those numbers drop significantly to 128MHB @ 15F and 162MBH @ 0F.



Now for the sizing question.  Everything I've read here is that you size the boiler to the EDR capacity.  After I install the insulation I don't need that much heating capacity.  Do I still go with a big boiler, replace the radiators with smaller ones so I can go with a smaller boiler?  I've not read anything on what to do when you have more EDR than you need due to improvements you made to the house.



thanks,

dave
· ·

Comments

  • JStarJStar Posts: 2,399Member ✭✭✭
    Heat loss

    Is this one or two pipe steam? One pipe, you are stuck sizing to the radiators. Two pipe, you can size to the heat loss and meter each radiator down with orifice plates.
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac.com
    http://facebook.com/thatcherhvac

    Guaranteed performance. Guaranteed energy savings.
    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    · ·
  • dpeartdpeart Posts: 31Member
    Two pipe

    system.
    · ·
  • JStarJStar Posts: 2,399Member ✭✭✭
    Two pipe

    Well, you're in luck. You can size the orifice plates based on the heat loss of each room. Then, you can size the boiler to the new ratings. This will also allow you to remove all of the thermostatic radiator traps, eliminating costly maintenance and service.
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac.com
    http://facebook.com/thatcherhvac

    Guaranteed performance. Guaranteed energy savings.
    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    · ·
  • Tim_HodgsonTim_Hodgson Posts: 59Member
    Steam Main piping

    Your system piping was probably sized for the connected EDR of the radiators. Remember to size the boiler for the large mains AND the heat loss.



    Best regards,



    Timothy Hodgson
    · ·