Paul SPaul S Posts: 509Member
Hey everyone.... This question is regarding a snow melt system with a mixture of 30% glycol....from the manifold through the 5/8" pex loops (6 of them) the GPM for all 6 of them is 6.84 GPM(1.14GPM per loop)....The head loss for the MANIFOLD is 4.5 ft HD....my question is how do I figure the size of the pipe from boiler to manifold (snow melt load=81,225 btuh/h) do I use 1"?....and how do I find the head loss from boiler to manifold, and do I add it to the 4.5 ft hd from the loops?....need this to size pump...thanks Paul S
· ·

Comments

  • GordyGordy Posts: 3,722Member ✭✭✭✭
    Supply return piping

    Should be sized to carry the BTUs, and flow rate required for the load. Yes the supply/return piping is additive to the manifolds head loss.



    You might squeak it out of 1" with a bigger circ, which brings higher head losses, or go to an 1 1/4, and get buy with a smaller circ.
    · ·
  • Paul SPaul S Posts: 509Member
    gordy

    Thanks for response....so if I use 1" 1/4"pipe because using 1" would be at it's max with 82000 BTUs.....how would I find the head loss of the 1" 1/4"pipe it's about twenty feet both ways and about 6 elbows?...thanks Paul S
    · ·
  • GordyGordy Posts: 3,722Member ✭✭✭✭
    Calculations

    http://www.copper.org/publications/pub_list/pdf/copper_tube_handbook.pdf



    http://mobile.engineeringtoolbox.com/



    To invaluable links.



    In the copper .org hand book you will find head loss for various pipe sizes fittings , and types of copper pipe. Enjoy
    · ·
  • RichRich Posts: 1,160Member ✭✭✭
    Can you say

    Snow melt using a Bumble Bee Circ . 42 watts to melt snow ? If you can keep the head pressure in the S&R section below 4 ft you can use the Bumble Bee for this system and keep the Delta T wherever you want it .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC 732-751-1560
    Serving most of New Jersey , Eastern Pa .
    Consultation , Design & Installation
    Rich McGrath 732-581-3833
    · ·