Too much to list

gcp13gcp13 Posts: 105Member
Not sure what they were thinking

I don't know where to start

2 in header?

Bullheaded tee,no swing joint

16 in. A Dimension

Level mains and back pitched drip returns

Main air vents 27" above waterline, above boiler

Plugged pigtail & 3/4 90 for presuretrol

Hartford loop close nipple 2 " above waterline

Auto feeder wired wrong not working
jpg
jpg
image.jpg
0B
jpg
jpg
image.jpg
0B
jpg
jpg
image.jpg
0B
· ·

Comments

  • kevinkevin Posts: 60Member
    boiler

    Looks like that boiler should be in a pit.
    · ·
  • JStarJStar Posts: 2,500Member ✭✭✭
    Steam

    This is why drop-headers were invented. But, then again, knuckleheads think a dropped header is just a way to get a bruised toe.
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac.com
    http://facebook.com/thatcherhvac

    Guaranteed performance. Guaranteed energy savings.
    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    · ·
  • kevinkevin Posts: 60Member
    drop header

    A drop header wouldnt work there, He said there is 16 in of a dimention. It needs to be in a pit or needs a condesate pump.
    · ·
  • ChrisJChrisJ Posts: 3,531Member ✭✭✭
    Header and pump

    In my opinion it needs a drop header and a condensate pump.
    Weil-McLain EG-40 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment Typical operating pressure 0.5 - 1.0 inch wc.

    Steam system pictures updated 1/25/15.
    https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#

    Don't push the envelope, eliminate it.
    · ·
  • Hap_HazzardHap_Hazzard Posts: 1,241Member ✭✭
    Hartford Loop?

    It looks like a completely dry return to me. Probably not a good idea with that A dimension. It probably calls for water mid-cycle, so add "fluctuating water line" to the list of troubles.



    I'm not sure how you measured that A dimension. Is that from the max water line to the header? If there's more than 28" from the water line to the main a drop header should work.
    1983(?) Peerless G-561-W-S



    3" drop header, CG400-1090, VXT-24
    · ·
  • gcp13gcp13 Posts: 105Member
    A dimension

    I measured A dimension from where the

    Feeder satisfies the lwco.

    At that point it was 2 in below Hartford loop

    Close nipple

    It was a toss up weather to raise up above

    Close nipple or get as much distance as possible.

    I would like to pipe the drip down into a wet return and then back to the boiler

    Customer doesn't want to do any work yet ???
    · ·
  • nicholas bonham-carternicholas bonham-carter Posts: 5,577Member ✭✭✭
    Bad install

    What were the symptoms which led to the service call?--NBC
    · ·
  • gcp13gcp13 Posts: 105Member
    Check heat

    Check heat for the season
    · ·