To get email notification when someone adds to a thread you're following, click on the star in the thread's header and it will turn yellow; click again to turn it off. To edit your profile, click on the gear.
The Wall has a powerful search engine that will go all the way back to 2002. Use "quotation marks" around multiple-word searches. RIGHT-CLICK on the results and choose Open Link In New Window so you'll be able to get back to your results. Happy searching!
In fairness to all, we don't discuss pricing on the Wall. Thanks for your cooperation.
Too much to list
gcp13gcp13 Member Posts: 117
Not sure what they were thinking
I don't know where to start
2 in header?
Bullheaded tee,no swing joint
16 in. A Dimension
Level mains and back pitched drip returns
Main air vents 27" above waterline, above boiler
Plugged pigtail & 3/4 90 for presuretrol
Hartford loop close nipple 2 " above waterline
Auto feeder wired wrong not working
  • kevinkevin Member Posts: 61
    boiler
    Looks like that boiler should be in a pit.
  • JStarJStar Member Posts: 2,668
    Steam
    This is why drop-headers were invented. But, then again, knuckleheads think a dropped header is just a way to get a bruised toe.
    - Joe Starosielec
    [email protected]
    drop header
    A drop header wouldnt work there, He said there is 16 in of a dimention. It needs to be in a pit or needs a condesate pump.
  • ChrisJChrisJ Member Posts: 7,575
    Header and pump
    In my opinion it needs a drop header and a condensate pump.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    If you even insult my steam system in a dream, you better wake up and apologize ò¿ó
    Steam system pictures updated 1/25/15.
    https://goo.gl/photos/ZgpNUTyckkmiEdAf9
  • Hap_HazzardHap_Hazzard Member Posts: 1,349
    Hartford Loop?
    It looks like a completely dry return to me. Probably not a good idea with that A dimension. It probably calls for water mid-cycle, so add "fluctuating water line" to the list of troubles.
    I'm not sure how you measured that A dimension. Is that from the max water line to the header? If there's more than 28" from the water line to the main a drop header should work.
    1983(?) Peerless G-561-W-S
    3" drop header, CG400-1090, VXT-24
  • gcp13gcp13 Member Posts: 117
    A dimension
    I measured A dimension from where the
    Feeder satisfies the lwco.
    At that point it was 2 in below Hartford loop
    Close nipple
    It was a toss up weather to raise up above
    Close nipple or get as much distance as possible.
    I would like to pipe the drip down into a wet return and then back to the boiler
    Customer doesn't want to do any work yet ???
  • Bad install
    What were the symptoms which led to the service call?--NBC
    Check heat
    Check heat for the season
Welcome
It looks like you're new here. If you want to get involved, click one of these buttons!