Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
New control help
Options
Schlitz
Member Posts: 1
I'm installing central AC, into my forced hot air system. I need to install a R8184M control in place of the R7184B control need some wiring help. Have new T-stat and wires installed, from T-stat to the new R8184M controller. Do I just jump the red and white wires from the new control to the old Red/white connections?
0
Comments
-
Don't do it
there is an A/C adapter for the R7184 series that includes the transformer and extra terminals you need.
If you use the R8184M, you'll lose the valve-on delay feature that the manufacturer specified. That can cause operational problems and warranty issues.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements