Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

New control help

Options
I'm installing central AC, into my forced hot air system.  I need to install a R8184M control in place of the R7184B control need some wiring help. Have new T-stat and wires installed, from T-stat to the new R8184M controller.  Do I just jump the red and white wires from the new control to the old Red/white connections?

 

Comments

  • Steamhead
    Steamhead Member Posts: 16,835
    Options
    Don't do it

    there is an A/C adapter for the R7184 series that includes the transformer and extra terminals you need.



    If you use the R8184M, you'll lose the valve-on delay feature that the manufacturer specified. That can cause operational problems and warranty issues.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
This discussion has been closed.