New control help

SchlitzSchlitz Posts: 1Member
I'm installing central AC, into my forced hot air system.  I need to install a R8184M control in place of the R7184B control need some wiring help. Have new T-stat and wires installed, from T-stat to the new R8184M controller.  Do I just jump the red and white wires from the new control to the old Red/white connections?

 
·

Comments

  • SteamheadSteamhead Posts: 9,215Member ✭✭✭✭
    Don't do it

    there is an A/C adapter for the R7184 series that includes the transformer and extra terminals you need.



    If you use the R8184M, you'll lose the valve-on delay feature that the manufacturer specified. That can cause operational problems and warranty issues.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    ·