Joist Trak or Radiators?

I am exploring the options for replacing the forced air heating system in a clients home. I am specifying the 86k btu TT Prestige Excellence with indirect DHW for a house with a design heat loss of about 54k.

The quandary is do we tear down the finished basement ceiling and install Joist Trak under the squeaky 1927 vintage subfloor and 3/4" hardwood flooring / carpet / tile or put in Runtal or Buderus wall mounted radiators?

My concerns are:

1. Does underfloor radiant work well enough with 1 1/2" of wood on top?

2. What will it do to the flooring in terms of expansion and contraction?

3. Will wall mount radiators with thermostatic valves be any more or less efficient at emittance?

4. Will the Joist Trak system make noise as it expands and contracts?



  • RichRich Posts: 1,626Member ✭✭✭
    Panel rads

    with TRVs would be my choice if faced with your concerns . Quality system , plenty zones , great comfort . No downside unless your homeowner really wants radiant floor
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC 732-751-1560
    Serving most of New Jersey , Eastern Pa .
    Consultation , Design & Installation
    Rich McGrath 732-581-3833
  • SWEISWEI Posts: 5,544Member ✭✭✭✭
    Design heat loss of about 54k

    Would lead me rather directly to the PTS 60 with its DOE output of 54k.  Indirect sizing would be based on calculated DHW demand.

    Agree that TRVs on panel rads are an elegantly simple answer.  Size them for 140F if possible.
  • SwampgasSwampgas Posts: 8Member
    PTS 60

    Would that be the Prestige Solo 60 w/ Trimax? Isn't that rated at 47k output and 54k input?

    I've used the TRV's before but never the underfloor radiant, is it inferior to a TRV system or just more expense and work?

  • SWEISWEI Posts: 5,544Member ✭✭✭✭
    edited July 2013

    Is indeed a Prestige TriMax Solo, with a 60k firing rate.  DOE output is 54k.  I=B=R output is 47k, but nobody I know of uses those numbers any more.

    A TRV is a control valve that attaches to a radiator and provides proportional regulation of the room temp using no electricity.  No relation to underfloor radiant, though they can be paired with it.  I'd say that 99% of them are probably installed on radiators.
  • SwampgasSwampgas Posts: 8Member

    I know the TRV's are for radiators, I was just pondering the efficiency of a system with panel radiators and TRV's vs a zoned underfloor radiant system like Joist Trak.

  • GordyGordy Posts: 4,139Member ✭✭✭✭
    Thinking of

    Pushing radiant through 1 1/2" of flooring . Decreased output, and increased water temps.

    So the big question is there enough floor area to meet the load at the potential output of the proposed radiant floors with that much resistance.