Can someone explain to me how the cold weather affects super heat and subcooling? Thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
347-692-4777
ASMHVACNYC.COM
cold temps
looks like no one wants to take this one on.0 -
Passing thru
Cold temps affects the subcooling because each cubic foot of cond air is colder than the minimum ambient temp the system was designed for. A c.f. of 40* air pulls away too much heat from the cond unit than say a minimum allowable c.f. of 60* ambient air . So the subcooling increases, above and beyond what is "normal" , THE HEAD PRESS DROPS too low causing metering (TXV) problems.The SuperHeat does not change. Lets say the AC TXV has 12* of SH at 40* EvapTemp ,giving 52* suction line temp at the thermal bulb . Then put that same TXV in a medium temp walk-in box that has an ET of 20*f and the suction line at the TXV thermal bulb will be 32*f. A freezer w/ a ET of -10*f will have a suction line temp of +02*F.In real life the AC TXV is a little different than a REF TXV and slightly different than a Freezer TXV , but I hope you get my point.0 -
Cold Temps
Assuming you're talking about residential units, low ambients have a greater impact with a fixed metering device. Since there is usually very little load, a machine with a FMD is in danger of not having a high enough superheat to avoid liquid refrigerant coming straight from the evaporator into the compressor. TXVs are more forgiving, as their job is to ensure a constant superheat at the compressor. Now to the other side. If the SH is too low, the compressor has to work very hard to mash liquid (instead of vapor) enough to raise the refrigerant temperature high enough above ambient so we can de-superheat it in the condenser. Since we can't change liquid into a liquid, you can imagine what your high and low side pressures will be, as well as a practically non-existing SC. If the compressor doesn't give up chewing on all of that liquid, it certainly will running when it doesn't have any work to do.0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements