Repipe rad to loop?

FizzFizz Posts: 230Member
Thinking of repiping 2nd floor Richardson rad to loop on separate run.  Rad doesn't heat unless valve to add-on 2nd rad(not a Richardson) attached to lat B is completely turned-off.  The system is 2 pipe.  Apparently supply pipe doesn't support attached edr.  Good idea?  Hope attached primitive drawing helps.
jpg
jpg
Run off 1st loop.jpg
0B
· ·

Comments

  • Dan HolohanDan Holohan Posts: 11,944Moderator mod
    I believe

    I believe your A pipe would have to be 2" for this to work.
    Site Administrator

    dan@heatinghelp.com



























    Hug your kids.
    · ·
  • FizzFizz Posts: 230Member
    So keep

    all attached as drawing, just change size of A pipe?  Thanks for quick reply!
    · ·
  • Dan HolohanDan Holohan Posts: 11,944Moderator mod
    Sorry

    Should have also mentioned that the risers to each radiator should be 1" instead of 3/4".
    Site Administrator

    dan@heatinghelp.com



























    Hug your kids.
    · ·
  • FizzFizz Posts: 230Member
    No problem

    Appreciate your input, very helpful.

    Thanks.

    Fizz
    · ·