Reno

Options
I just put in 2 new peerless boilers with a domestic hot water coil. Both customers complain water comes out hot then goes luke warm. How much hot water does these coils put out? Can they handle a shower or are they only good for washing hands?

Comments

  • heatpro02920
    heatpro02920 Member Posts: 991
    edited April 2013
    Options
    what model peerless

    should be plenty of hot water, what are your limits set at? This sounds to me like a mixing valve issue, I hate to say it but maybe install error? do you have pics of how you installed the domestic piping... What mixing valve did you use, did you install a flow restrictor?



    When I do tankless coils, I install a FR in the cold inlet that is about 1/2gpm less than the coils gpm rating and install a good anti scald mixing valve {exactly as the instructions dictate} {taco t5002 works well}... Even a watts 70af works for 1/2 the price... Then set the limits to 165-185 {160-180 can work too depends on boiler, coil, and needs}.... no exceptions, you bend the rules with tanklesses you get bit, every time...



    Some coils have internal flow restrictors, and having 2 isnt a good idea, so check your instructions....



    One more thing are these steam or FHW boilers?