Pipe Length Confusion

SpockSpock Posts: 7Member
I find in various design guides references to the distance between the circulator, branch fittings and 90 degree fittings. But in practice what I see is components placed as close together as possible. This is particularly true in some of the integrated component structures where mounting flanges, tempering valves, check valves and branch fittings are all cast into a single component and designed to attach directly to a circulator.



An example is a design guide that says branches should be no closer than 8 pipe diameters from the circulator outlet, 90 degree fittings should be no closer than 6 pipe diameters from a circulator or branch, etc.



So which is it: Make it compact or follow the design guide? If the answer is follow the guide, then why do the compact designs work?
· ·

Comments

  • SpockSpock Posts: 7Member
    guess there is such a thing as a dumb question after all

    Hmmm. It would seem that either I've asked a really great question that has everyone stumped or one that is so simple it doesn't dignify an answer.



    I'm guessing the latter...
    · ·
  • ZmanZman Posts: 2,211Member ✭✭✭
    It works

    The attached file was originally posted by Mark Eatherton. I think it does a nice job of clarifying what is really important.

    I think you need to define "it works". Not following the rules will shorten the life of components and cause circulators to underperform. Air entrapment, ghost flows and cavitation are other issues. Technically the system is "working", it still is not good practice.

    Sometimes posts just don't catch anyone's attention. There was nothing wrong with your question,

    Carl
    jpg
    jpg
    resize_8 PRIMARY SECONDARY CRITICAL ELEMENTS.jpg
    0B
    · ·
  • SpockSpock Posts: 7Member
    Good Info...

    Thanks Carl. I appreciate the response and the diagram.
    · ·
This discussion has been closed.