fan coil units

keithkeith Posts: 40Member
How would i figure btu or edr of fan coil units on a steamsystem. There are six coils with fans on one zone of this system. The other zone is 2" baseboard elements. This boiler is about 27 years old and has a small leak at a push joint when it first starts up in the am. It will have to be replaced in the spring.
·

Comments

  • Dan HolohanDan Holohan Posts: 11,944Moderator mod
    Click on

    Conversion Factors at the top of the page.
    Site Administrator

    dan@heatinghelp.com



























    Hug your kids.
    ·
  • keithkeith Posts: 40Member
    fan coil units

    Thanks dan What forula should be used ???? The coils are all assorted sizes ??
    ·
  • Dan HolohanDan Holohan Posts: 11,944Moderator mod
    It's

    Steam Fan Coil Loads (in pounds per hour) = CFM X Delta-T of air (in degrees F), divided by 800
    Site Administrator

    dan@heatinghelp.com



























    Hug your kids.
    ·
  • keithkeith Posts: 40Member
    fan coil units

    thank you dan
    ·