Columbia Joins the Wet-Base Power-Gas Steamer Ranks
Steamhead
Steamhead Member Posts: 16,835
This was probably as bad as Hurricane Sandy got in the Baltimore area- certainly nothing like coastal New York or New Jersey, where entire neighborhoods were wiped out.
This basement flooded because the downspouts had been disconnected from the drainpipes that ran to the street, so all the water was dumped around the foundation. The ground got saturated from all the rain, the power went out so the sump pump quit,  and the basement flooded, knocking out the boiler and water heater.
We had optimized this system about a month ago with Gorton #2 main vents and Vent-Rite #1 adjustables in the bedrooms. So the owners called us to replace the boiler and water heater.
The boiler was a Columbia CEG-187, with the usual undersized copper abomination that was leaking under the insulation.
Consulting
    edited November 2012
    In with the New
    the owners wanted to install better equipment than they had.
    If this boiler looks like a Utica Starfire, it is..... Columbia re-brands Uticas for their cast-iron residential boiler line. This is a CSFHE-4100S with the familiar Carlin EZ-Gas burner, which has only recently been an option on these boilers. Boiler and burner were supplied together by the local Columbia store. This combination (as well as the smaller CSFE-0365S) is competitive, efficiency-wise, with the Smith 8 and Slant/Fin Intrepid series with gas burners, and since Columbia stocks these boilers and burners we didn't have to wait for them to arrive.
    We piped the drop header so as to make room for the chimney connector to pass underneath.
    The water heater is Bradford-White's M4-series 50-gallon, which has an 0.62 energy factor because of its heavier insulation, better baffling etc. as opposed to the usual 0.56-0.59.
    And of course we set both units up on blocks, to help avoid future flooding!
    Consulting
  • JStar
    JStar Member Posts: 2,752
    Boiler
    Nice! I like how the header squares up the whole system. What were your combustion numbers with that model boiler? The Starfire usually gets around 82%.
  • Steve_210
    Steve_210 Member Posts: 646
    Curiosity
    Nice job, just curious why you went with the water heater and not an indirect
    I'm guessing Budget
  • Steve_210
    Double post
  • Rod
    Rod Posts: 2,067
    Very Nice!
    That piping is a masterpiece! Very Nice!
    - Rod
    This one
    ran about 82% on the Testo, with the EZ-Gas running at 9.0% CO2. There was a bit of headroom available but we don't use it, since BG&E has been known to spike their wintertime gas supply with whatever they can get to meet the demand. The advertised AFUE on oil is 85.7%, probably a bit lower on gas.... still better than an atmospheric.
    Note that the same 4-section block can be fired at several different rates- 140,000 BTUH (used here, same as 1 GPH on oil), 175,000 (1.25 on oil) and 210,000 (1.5 on oil). Obviously the higher the rate, the lower the efficiency. Where this option exists, we always use the lowest rate for best efficiency and longer life.
    Consulting
    Bingo
    but we still get better efficiency than that old Rheem offered.
    Consulting
    The difference is
    which diffuser (burner head) is used. The higher rate would use an air tube with the "A" diffuser, the lower uses the "B" diffuser. The "A" diffuser also produces a longer flame than the "B" diffuser. There's also a 9-slot diffuser which splits the firing rate difference and produces a short, compact flame.
    Your Starfire is a 5-section and the actual firing rate is 245,000 BTUH (oil firing rate 1.75 GPH x 140,000= 245,000). If in doubt as to which diffuser to use, check with the Carlin people.
    Consulting
    Thanks!
    nm
    Consulting
  • Henry
    Henry Member Posts: 998
    Carlin burner
    We got stuck using a Carlin burner because it was in stock compared to a 4 week delay for a Becket. It was only problems! First it was the ignition card and then the modulation. We have never had so much problem with a burner. BTW, a very nice instal!
    Thanks, Henry
    which Carlin did you have? They work well for us.............
    Consulting
  • ChrisJ
    ChrisJ Member Posts: 15,676
    Beautiful
    job as always from steamhead and Gordo.
    I'm curious on your opinion as far as water heaters go. Our local supplier told me on a standard natural draft water heater he didn't recommend buying the thicker insulation as most of the heat goes up the chimney.  He said it was an ok idea on power vented models or models with a damper though.  I couldnt afford the better and went with the standard I think, 1" insulation on mine.
    I will admit, even though it only has 1" thick insulation my power vented Bradford White kept surprisingly hot water for 2 days when we lost power from Sandy.  We of course, used it sparingly.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    Only thing I can say
    is that on heaters with less insulation, the outside feels warm.
    With these, it doesn't. Enough said.
    Consulting
  • ChrisJ
    I see
    And that is why I asked. Because you always give clean cut answers with a good explanation.
  • Gordo
    Gordo Member Posts: 857
    Followup Details
    The return is tapped at 2", which is nice.  Here, then, we added a 2" x 6" extra heavy nipple and a 2" x 1-1/2" cast iron tee before transitioning to the 1-1/2" copper equalizer line.  The extra mass will tolerate corrosion better.
    The sightglass gets a proper blowdown valve and a drain hose.  Every sightglass should get one.
    The solenoid valve on the Hydrolevel VXT-120 was reversed to make it fit the existing feed line and replace the Unimatch.  That's a bit of a trick!
    We've asked the good folks at Hydrolevel to think about re-designing the solenoid mounting to make it easier to reverse.  That issue is still in the air.  We've seen too many VXTs mounted upside down or sideways by  "others".  It's such a nice piece of equipment, it deserves better, as well as making the numbers, it's raison d'etre, easier to read.
    It would be helpful if the folks at Columbia would add a bit of length to the pressuretrol whip it enable it to be more easily mounted higher above the waterline.  It is clear the way it is mounted now is called for by the packaging engineers and is not the optimal design for maintenance.
  • gerry gill
    gerry gill Member Posts: 3,078
    Another
    great looking job guys! Just curious, do you guys use any boiler water additives or just straight water?
    gwgillplumbingandheating.com
    Just water
    the water in this area is good enough that we don't need chemicals, at least on cast-iron boilers.
    Consulting
  • Gordo
    Undersized Copper Header
    The old boiler was installed by our local utility's sock puppet service arm, BGE Home.
    They have actually told customers of ours that their steam boiler installs are done properly.
    We have yet to see any install by them where that was true.