ES2 venting?
jonny88
jonny88 Member Posts: 1,139
Hi and a happy thanksgiving.I got a ? with an ES2 Burnham.Usually when i put them in i use an Alliance for hot water.With the hurricane etc and loss of power for 2 weeks i am getting customers who want to use a hot water tank as they will have hot water in case of an outage.how do I vent the water heater into the same chimney as the ES2.The boiler comes with its own flue pipe.Is it possible to use a heavy gauge flue pipe to combine boiler and water heater eliminating supplied boiler vent pipe and run the two units into the new liner.Thanks for your time.
    Steamhead Member Posts: 16,835
    You should be able
    to put a tee near the chimney opening and tie both units in there. But first, is the chimney lined properly? ES2 boilers have low enough stack temps that an unlined chimney will run too cool, causing condensation in the flue.
    Consulting
  • jonny88
    liner
    i use the stainless steel liner sized to the specs.thanks for the reply just wanted to ensure the tee could handle the venting as the provided vent is double wall.i sometimes use the taco pc700-2 outdoor reset with this boiler,whats your thoughts on this.people seem to be happy with it so far.
    The Taco ODR will work fine
    but we generally use the ODR card that Burnham sells for this boiler. It works just as well and saves some installation work.
    Consulting
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    SR501-ODR
    Take a look at the 501 w/ ODR, Burnham should reconsider their pricing on the EQ ODR module!
  • Jason_13
    Jason_13 Member Posts: 304
    IQ-ODR
    If I am using an IWH I find that the price is comparable to any other that has same features plus the ease of installation.
