Solia boiler question?
Eric L._2
Member Posts: 94
Replace and converted coal boiler about 2 years ago in my relatives house and it heats fine but I can't get the water temp of the boiler to get much over 140 degrees. I ran a heat calc and I chose the appropriate size according to that. Like I said it heats fine but there are some big pipes supplying all the rads. I believe the feeds are 2 inches with 1/2 inch branches.What could cause a boiler to not reach set temp of 180 deg? Thanks
Eric
Eric
No
primary/secondary? The boiler will be destroyed by condensation without protection from the low water tempsTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Cold temps
What type of boiler is this? Need some more info on this.There was an error rendering this rich post.
It is a Solia Boiler model
SL375 0.75
Beckett AFG .60 x 70°B
105,000 91,000 79,000 526 85.5 3.6 300 21” x 33” x 22”
I piped it just like the manufacturer recommended and it does have an adjustable bypass to divert some hot feed to cold return but even with that my temps don't get up much over 140 degrees.0 -
You
need primary/secondary or a low loss header. You can't run a non condensing oil boiler with those temps,it will have a VERY short life!To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Water temps
I looked at the Mfg recommended piping. Do you have a indirect on it? Running at that return temp isn't good. What did the Mfg tell you?There was an error rendering this rich post.
Piping
What type of radiation is in the building? What was the heat loss. Do you have the proper nozzle per the heat loss?
If you have a large water volume system, which it sounds like you do have, you may need a boiler bypass. The boiler can only handle a certain amount of flow. There is a minimum and maximum flow. Exceed that flow and the water temperature may not get high enough. A boiler bypass will bypass water around the boiler and back to the system.0 -
It may be
that the water temps you are seeing are all that's needed to heat the house. Many older hot-water systems run like that.
In your case, I'd favor an injection-loop setup. This uses a small variable-speed pump to move some water from the boiler loop (which runs at a high temperature) to the system loop (at a lower temperature). The pump speed is regulated by an outdoor-reset control which can adjust the system loop temperature according to the outdoor temperature.
Outdoor reset is a proven fuel saver. With this setup you'd accomplish two things- boiler minimum temperature and optimum system temperatures.All Steamed Up, Inc.
Consulting0 -
Temp
Have to figure out from the Mfg what the min temp of the boiler is, I install Buderus and they allow low return temps, not sure on this boiler. Like Steamhead said you need a injection loop to keep temps to the boiler up.There was an error rendering this rich post.
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
