To get email notification when someone adds to a thread you're following, click on the star in the thread's header and it will turn yellow; click again to turn it off. To edit your profile, click on the gear.
The Wall has a powerful search engine that will go all the way back to 2002. Use "quotation marks" around multiple-word searches. RIGHT-CLICK on the results and choose Open Link In New Window so you'll be able to get back to your results. Happy searching!
In fairness to all, we don't discuss pricing on the Wall. Thanks for your cooperation.
Hart & Cooley Ultravent
SpeyFitterSpeyFitter Member Posts: 420
Anyone in here run into this stuff? I just ran into this stuff for the first time today. It was on a foreclosure. The previous owner(s) duct taped the failed joints, and the pipe was super brittle and very easy to crack which is evidence enough of overheating. It was plastic vent pipe on an 83-84% efficient appliance (cast iron Slant Fin Boiler with an inducer fan). Research shows there may be a recall on it. Anyone else run into this crap?
Class 'A' Gas Fitter - Certified Hydronic Systems Designer - Journeyman Plumber
  • Mark EathertonMark Eatherton Member Posts: 5,493
    edited January 2011
    Ultravent and Plexvent have both been recalled....
    They will pay some monies towards the replacement, but it barely covers your labor costs.
    ME
    P.S. Here is a link to the CPSC web site explaining the process....
    http://www.cpsc.gov/cpscpub/prerel/prhtml06/06022.html
    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • kcoppkcopp Member Posts: 2,524
    I installed a....
    boatload of it on Burnham 2PV's 10- 15 yrs ago... It was ok. It was also know by  Plexvent by Plexco....Not the easest to cut properly w/o cracking. Most of the problems I saw were on dried up silicone. Saw one job I installed that still had the original venting... just w/ dried up silicone. Vent was intact.
     Yes there was a recall... and a HUGE replacement campaign. Burnham again went abouve and beyond to make it right. A ton of other mfg used it also.
  • IronmanIronman Member Posts: 3,133
    Corrective Action Program
    The Federal government had a corrective action program where they made the equipment manufacturers as well as Hart and Cooley, and whoever else made this stuff, cough up the $$$ to have all of it replaced. A licensed Gas/ HVAC contractor would get the necessary B vent, power venter and draft regulator from his local supply house and the fund would cover the materials but not any labor. Or the customer could get $400 toward a new appliance.
    We ran into one last winter and the 800 number for the program was still active, but they would not give the customer any $$$ towards a new furnace.
    It's absolutely mandatory that the UltraVent be replaced.
    Bob Boan
Welcome