oil now .. gas later?
jpf321
Member Posts: 1,568
in Gas Heating
I'm looking for a possible recommendation for a boiler to replace my old beast .. I have a Fitzgibbons 402 (rated for 700sf of steam) .. currently oil fired for a 1-pipe steam system.
This summer, I'd like to replace the current boiler with a new steamer .. however, I'm looking for one that will accept OIL now .. with the potential to convert to GAS later .. do these things exist?
A neighbor of mine recently did an oil-->gas conversion on a 23yr old Peerless boiler. I don't have specifics better than that.
Thanks, jpf
Thanks, jpf
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
Sure they do
we frequently install them. The Slant/Fin Intrepid and Smith 8 series are approved with oil and gas burners.
Refresh my memory, how much radiation do you actually have?All Steamed Up, Inc.
Consulting0 -
371 sqft EDR
Thanks Steamhead .. it's in the sig .. but I measured 371sqft EDR. As well as 120lf of 2in main pipe + about 100lf of 1-1/4 risers.1-pipe Homeowner - Queens, NYC
my NEW system pics | my OLD system pics0 -
You'd want
a Smith 8-S-4L, at 413 square feet EDR, or a Slant/Fin TR-30, rated 421 square feet.All Steamed Up, Inc.
Consulting0 -
thanks but .. confused ..
my rads come to 371sf EDR ... but what about "+33%" for pickup factor?
then I get 371 x 1.33 = 493 .. or perhaps i shouldn't figure in the 1.33..or perhaps you figured in the length of the mains somehow.
thanks, just trying too understand.1-pipe Homeowner - Queens, NYC
The pickup factor
is already built into the boilers' Net ratings. You do not need to add any more, unless you have wildly oversized piping or some other factor. In almost all cases the built-in factor is plenty.All Steamed Up, Inc.
Consulting0 -
ok thanks....
after reading the literature on them today, I did notice that it said something about 1.333 as a footnote, but thank you for clarifying it for me.
one further question since we're on the subject ..
what's your preference:
float or probe LWCO?
I see that the Smith 8 comes with either Beckett, Carlin or Riello...and it says optionally a 2-stage "fuel unit".. do you have preferences here? Do you think the Carlin EZ-H2L may be available on the Smith 8 in next 8months? Would that be the ideal situation?
I don't see the burner options that the Slant/Fin offers .. but I do see they also have an optional 2-Stage Fuel Pump. I do like the fact that Slant/Fin is based within 20mins of my house in Greenvale, NY.
Thanks for your experienced thoughts on the subject.1-pipe Homeowner - Queens, NYC
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 130 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
