VFD pump versus bypass valve
Hvacman
Member Posts: 159
Both will do the job but I think you will find the drive to be a more expensive way to go. Even though the cost of drives have dropped and you will see a modest energy savings from using a drive I think the BP valve is the way to go.
Just wondering what your opinions are on versus the other. 24 unit apartment house, constant circ., zone valves on baseboard, mod/cons, outdoor reset, supply and return temp. sensors, one space sensor for reset. More information needed? Pump is 1 1/2 hp B&G.0 -
Cost
Cost is always a concern. Not so much as reliability. If reliability is comparable, would electrical savings make up initial instalation costs?0 -
Cost Versus Value
Most VFD applications below code threshold are rebate eligible at least here in MA. Your local utility would have more information.
You have to know and crunch the numbers, what your current actual draw is (brake HP or kW, not nameplate HP). How many hours of operation at what settings.
VFD's are way down in cost these days but if you are going to install a VFD, the motor of the pump has to be inverter-compatible which means a motor change if not a pump change.
This is what I would do: Figure out your actual flow rate and head which satisfies the building load. Be as accurate as you can. If you have a current pump curve, figure the amps, delta-P and know the impeller size (dead-head the pump momentarily to determine the no-flow, maximum head. This will tell you the pump impeller size if you have a good curve from the manufacturer.)
Then, select an ECM motor pump, such as by Wilo or Grundfos. These have, as features on the right models, integral Delta-P sensors. Dial-in and enjoy the savings.
I would hope that your control valves are two-way and not three way. If three-way, the use of Delta-P becomes moot.0 -
I forgot...
I forgot the VS pumps now available... Others can tell you application info, I peeked at the Wilo site but the range of products is enormous. I've not used them but are an interesting option to me vs. a "normal" pump with separate VFD. See post below for payback ideas, will depend on many factors.0 -
I am with Brad, Wilo or Grundfos, Delta p. 3 way valves will
mess up the savings so forget it if 3 way valves. I think perfect application. Other way is 3 phase 1.5 hp motor and maybe Danfoss vfd but this gets expensive along with a pd transducer. Go the ECM route and will be a winner.0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
